alienencounters said:
110 plus 110 equals 220

Last but not least the reason that europe is on 220 and not 110 is because its actually SAFER. Voltage doesn't kill CURRENT kills - the EMF to run a 1 hp motor is constant - but at 220V you need half the amperage. Total power is the same, but in the even of an accident the lower a breaker is set to trip at the easier it is to trip.

Not quite

Amperage kills, yes, however,


I =V/R

I = amperage
V = voltage
R = Resistance

Assuming the resistance of your body does not vary (it does, but not alot, and only over time)

with R being constant, the higher the V, the higher the I.

In Europe, the V is higher, hence it is more dangerous.

Don't believe me, grab hold of a 125 Kv line and see what happens.
 
data1960 said:
best to hire a pro for your home work.

I disagree with that.

There are lots of hack electricians out there. I've seen them. I might say ok if you said, always hire a pro who knows what he is doing, or does a good job.

If you don't know what you are doing, then yes, hire a pro. If you are unsure, then hire a pro.

But if you know what you are doing, then I have no problem if you do it yourself.
 
Papi Chulo said:
There is absolutely nothing wrong with aluminum wire.. when installed & used correctly

True, however, try finding light switches and recepticles for aluminum wiring. You have 1 choice - coalr, and they cost about 5 bucks per switch and are available only in the old toggle style.

Try finding a dimmer switch.

You can pig tail it to copper at the box I suppose, but that is not always feasible or a good idea.
 
james t kirk said:
You can pig tail it to copper at the box I suppose, but that is not always feasible or a good idea.


a dimmer?.. many dimmers come with leads of tinned copper which can be connected to aluminum wire using an approved connector and anti-oxidant.

try to find a decorator device!!!


Pigtails using proper connectors are acceptable... and they work
 
Papi Chulo said:
a dimmer?.. many dimmers come with leads of tinned copper which can be connected to aluminum wire using an approved connector and anti-oxidant.

try to find a decorator device!!!


Pigtails using proper connectors are acceptable... and they work

Yes I know, but the dimmer will also have the Al symbol stroked out.

I've tried wiring the dimmers at a friend's house with the grease in the marrette even and after about 6 mos. to a year, the dimmer isn't working anymore. And I mean every dimmer too.

Pigtails are acceptable, but you need the grease and it really clogs up the box which are often packed already with wires. Add some marrettes in there and it's very difficult.

As you stated, the aluminum can be made safe, but the wire has to wrap around the lug perfectly and there can not even be a notch in the aluminum conductor where maybe the wire strippers nicked the conductor.

Copper is far more forgiving.
 
data1960 said:
I agree, but I believe this is self-evident. The whole home renovation industry has taken a beating as a result of hack trades. Even some of Mike Holmes' recommended trades are under scrutiny.

.

I hired one of the "trades" from Holmes on Homes to remove and replace my existing aluminum soffit, fascia, eaves trough, etc.

I called up 3 of his recommended trades for aluminum siding. Philip Lemieux, Avenue Road Roofing, and Better Contracting. All 3 gave me prices, which included removing and replacing the wood fascia boards - which was my main problem, the eaves were literally falling off the roof.

I didn't hire Lemieux, and Avenue was too expensive. So you figure out who I hired.

Let's just say that what you see on the show and what you get when you hire one of Holmes' trades are 2 vastly different things. On the show, they show up with 10 guys, with matching T shirts, with fall arrest harnesses, and "the fat guy" just stands there and shakes his head and can't stop mouthing off about how bad a job the original contractor did.

In reality, "the fat guy" never even swings by your house. You get one skinny ass white guy from Oshawa who "the fat guy" had sold the job to. The skinny guy shows up with his whacky girl friend who sits in the van all day and smokes and talks on her cell phone.

The skinny white guy does all the work himself. No fall arrest harness, no-one to help him out, no-one to even call 911 if he falls off the ladder while trying to hold and nail a 2 x 6 x 12' long new fascia board by himself.

I ended up helping this guy because it was killing me to watch and I wanted the job done properly. I had to tell him to put more nails in, to mark where the rafter tails were so he could find them rather than just guessing and driving nails into air. Then I helped him rebox in a couple of beams because he was doing it wrong, then I cleaned up for him because he couldn't be bothered.

Fortunately, the fat guy had subbed the eaves to a different guy who did a very good job.

So, moral of the story, good luck when hiring trades....
 
james t kirk said:
So, moral of the story, good luck when hiring trades....


Keep in mind that you can write NO SUB-CONTRACTORS TO BE USED ON THIS JOB. ALL WORK WILL BE DONE IN COMPLIANCE WITH LOCAL, PROVINCIAL and FEDERAL LAWS.

A contractor works for you and not the other way around.
 
tboy said:
LOL @ 20 ga....if you've seen, or used 20 ga in a house, you should be arrested for reckless endangerment......now really, who doesn't know what the fuck they are talking about?


I find it funny that you laughed at me saying 16 ga when you come back with 20...lol.... (I couldn't remember the normal 14/2 numbers at the time, so sue me).

My bad, I meant to say 12ga. When I said 20 ga. I had 20 amps on the brain which is the correct amperage for a 12 ga. wire.







Point out WHERE on this thread I attacked anybody?[/quote]
 
baci2004 said:
My bad, I meant to say 12ga. When I said 20 ga. I had 20 amps on the brain which is the correct amperage for a 12 ga. wire.







Point out WHERE on this thread I attacked anybody?
[/QUOTE]

LOL which was my excuse in a couple of threads....

Hence, why, unless I'm simply installing a ceiling fan or fixture, I hire someone who knows what they are doing.....
 
My house has aluminum wiring, which I was not too happy to discover when I bought it. But it is ok, you just have to use the CuAl marettes. I have replaced all the dimmers and many fixtures, and it all works ok.
 
No shit about the home inspectors....I was recently involved in renos on a house that was inspected and the inspector didn't find:

The hole in the roof (about 12" square)
The light switches in the kitchen that were just screwed to a piece of masonite and mudded to the wall
The light fixture in the kitchen held in place with electrical tape
The front room pulling away from the main part of the house
among other things.

Home inspection is a joke IMO....I saw a home buyer's inspection kit put out by the ontario government and I think it should be a mandatory handout by all realtors to home buyers..
 
tboy said:
LOL oh really? and where will the electrons go from the two 110 hots? Into space?

Dude, how it works is:

The electrons flow from the hot, through your equipment, to the neutral. If you don't connect the neutral, they won't go anywhere....the ground in Canada is to prevent shock by making sure the metal components of all appliance is connected to the box in the wall, which is connected to the service panel, which is, ahem, attached to the ground.

FYI: the neutral is also referred to as common, or return.

And people ask me why I say always leave electrical up to the pros?

Sorry wrong.

Want proof? Disconnect the neutral on your stove. All the 220/240 volt bits and pieces will still work (Large elements, furnace). Only the 110 components will not work.

Basic problem is much simpler. You never ever ever plug something rated at 15 amps into a 30 amp circuit. If you do and anything goes wrong you risk a giant mess. Also your house insurance will not pay out for any damages because you contributed to them.

If you do it you need to add a nice small fuse to the circuit.

RE 50 / 60 creating issues. Yes it might. Step up transformers do not fix the frequency issue either.
 
Wait a second loki: you're saying that you cannot plug a 5 amp light into a 15 amp circuit? LOL.....you got that backwards dude: one shouldn't plug something that draws 30 amps into a 15 amp rated circuit.

And you are right, I was mistaken, I should have said, in a dc circuit, the electrons flow from the hot/live wire to the neutral. In an alternating current circuit they go both ways......(hence why it is called alternating).
 
tboy said:
Wait a second loki: you're saying that you cannot plug a 5 amp light into a 15 amp circuit? LOL.....you got that backwards dude: one shouldn't plug something that draws 30 amps into a 15 amp rated circuit.

And you are right, I was mistaken, I should have said, in a dc circuit, the electrons flow from the hot/live wire to the neutral. In an alternating current circuit they go both ways......(hence why it is called alternating).

I think I expressed it correctly. If you plug your toaster into a 15 amp/110 volt circuit and anything goes wrong you blow a fuse. Might damage the toaster or cord. You plug a toaster into a 30 or 40 amp circuit and anything goes wrong wires melt and fires can start. Back to the stove…. They have fuses inside them to limit the amperage going to the 110 plug. You need some fuses to protect the outlet.

But just for fun, let’s go off on a tangent. Last week I was at an education session and watched a very kinky and sweet innocent looking young lady fondling about 100,000 volts. The major effect was making her giggle and look around for someone to use it on.

Do any of the local experts want to explain why she did not fry?
 
static electricity produces no current........which can be produced relatively easily using a van der graf generator.

As for your circuit/current situational example. If something goes wrong with the toaster, such as a short, the 30 or 40 amp circuit breaker will blow before anything too dangerous happens (for eg: a short in the toaster). If you're worried about the wiring inside the walls melting or creating enough heat to melt or cause any surrounding materials to combust the wires outside the walls (the cord leading to the toaster) will act like a fusible link. Yes, fires can result but we are talking about when something seriously wrong happens, not during normal use.

For eg: you can plug something into a 15 amp circuit that draws 40 amps, but the circuit breaker will flip the second you turn it on. Hence why we have different gauges of wire, different types of circuits which is basically why there are so many regulations in regards to circuits in a home.
 
If you plug a 15 amp toaster into a 30 amp toaster and for some reason the toaster draws say 25 amps, the toaster will melt, the wires in the wall will be fine as they are rated for 30 amps.

The problem is as tboy says, if you plug something that draws 25 amps into a 15 amp circuit, the breaker trips (hopefully) or the fuse blows (it will if the fuse has not been changed out to a 30 amp fuse.

Fuses actually offer better circuit protection than a breaker since a fuse will always blow whereas breakers can sometimes stick. The problem with fuses is that sometimes dumbass homeowners put a 30 amp fuse into a 15 amp circuit to stop that annoying trip to the basement every time the fuse blows because the old lady's got the frying pan and toaster plugged into the same recepticle. Now you have the makings of a fire.

There is nothing wrong with a good fuse panel, provided the proper sized fuses are used.

Since we are on the topic, many of the older homes in Toronto feature the infamous "knob and tube" wiring. I have a friend who bought an old house off of Gerrard and I told her to have it rewired as it was almost all knob and tube, or worse, fucked with knob and tube. She didnt' listen, the house caught on fire. It was the new wiring that actually caught on fire. Of course, it had been spliced into the old knob and tube.

You'd think then that she'd have the place rewired (after the insurance company repaired the 2 rooms where the fire was). But no, a trip to Thailand was more to her liking than proper wiring.
 
With most audio equipment there is a universal power supply. There will be a sticker or printed specs on the back of the unit. Depending on the age of the unit there may or may not be a switch. Its best just to take the unit to Bracks or any good hi-fi place. NOT BEST BUY OR FUTURE SHOP. Go to a dedicated hi-fi shop where they can look at the unit and know what they are talking about. Chances are unless its very high end you will be able to plug it into your 110v outlet. If not You can change the transformer in the unit to a 110v. Dont plug it into your dryer or stove outlet the ground is different, the frequency is different and you may damage your unit or kill yourself, or both. If its a high end power amp designed for 220v like a schaller or audio-muller changing the qower supply will affect the sound in a very bad way as those units are designed around the 220v power supply. I made that mistake. I brought an audio-muller amp in england. It sounded great there, when I brought it back to Toronto and put in a 110v P.S. it sounded like a sony. I freaked out and called the manufacturer in germany, they informed me that all of their products are designed around a 220v power supply, thats why they don't sell them in north america. I was stuck with a $3500 german power amp that sounded like a $400 japaneese reciever. Boy was i pissed.
 
james t kirk said:
If you plug a 15 amp toaster into a 30 amp toaster and for some reason the toaster draws say 25 amps, the toaster will melt, the wires in the wall will be fine as they are rated for 30 amps.

if you plug something that draws 15A into a circuit that is wired and protected for 30A, it will not melt.

It will draw whatever current it needs to work, not the total current available. Now if there was a problem with the item and it were to draw more than it is rated for... then it could cause a fire as the protection for the circuit would allow it to use 30A
 
Papi Chulo said:
if you plug something that draws 15A into a circuit that is wired and protected for 30A, it will not melt.

It will draw whatever current it needs to work, not the total current available. Now if there was a problem with the item and it were to draw more than it is rated for... then it could cause a fire as the protection for the circuit would allow it to use 30A

I believe that's what I said, when I said, "and for some reason", i.e. there is a problem withe toaster that causes it to draw 25 amps, which is below the 30 amp rating of the supply circuit, hence the breaker that is rated for 30 amps on the supply circuit will not trip.

What that problem may be, I dunno. Just a problem that causes the toaster to draw 25 amps, well above what its supply cord will be rated for, yet below the 30 amp rating of the supply circuit.
 