squirrelly04 said:
I don't think you know what you a talking about, maybe you should call an electrician!
Air conditioners are 240 volts. They don't have a neutral. How do they work? Maybe the electrons go into space?

same as stoves, driers etc, the only reason they have a neutral is because 110v is used for controls, lamps etc . I believe that in the US their stoves & driers are simply 220v, where Canadas are 110/220
 
Gentle Ben said:
same as stoves, driers etc, the only reason they have a neutral is because 110v is used for controls, lamps etc . I believe that in the US their stoves & driers are simply 220v, where Canadas are 110/220
I knew that.
 
squirrelly04 said:
I don't think you know what you a talking about, maybe you should call an electrician!
Air conditioners are 240 volts. They don't have a neutral. How do they work? Maybe the electrons go into space?

LOL that's funny, my a/c unit is 120......I love it when people make statements like: airconditioners are 240....lol Is that like: all vehicles run on gasoline?

Here's a good read....now, in an alternating current circuit (which I failed to specify) the actual flow of electrons reverses and then goes forward then reverses hence why it is called alternating current.

http://www.play-hookey.com/ac_theory/

Here's another good read:

http://en.wikipedia.org/wiki/Electricity_distribution

Where the hell is rubmeister to put this all to bed?

As for 220/240 using smaller wire...that's funny! every circuit I've ever seen that provides 240V is 10 or 12 gauge and the rest of the house is 14 or 16 ga.....

Man I love how people come on here sprouting off shit like this.....
 
tboy said:
LOL that's funny, my a/c unit is 120......I love it when people make statements like: airconditioners are 240....lol Is that like: all vehicles run on gasoline?
My first thought was squirrelly04 was referring to central AC , not room air conditioners, and yes, they run on 220!
 
tboy said:
LOL that's funny, my a/c unit is 120......I love it when people make statements like: airconditioners are 240....lol Is that like: all vehicles run on gasoline?

Here's a good read....now, in an alternating current circuit (which I failed to specify) the actual flow of electrons reverses and then goes forward then reverses hence why it is called alternating current.

http://www.play-hookey.com/ac_theory/

Here's another good read:

http://en.wikipedia.org/wiki/Electricity_distribution

Where the hell is rubmeister to put this all to bed?

I wasn't talking about a window air conditioner.

I was talking central air.

Are you an electrician?
 
Watt a charge I get out of threads like the current one where there's resistance to an idea.

DC what I mean?

(I know, my puns are revolting.)

Carry on....
 
squirrelly04 said:
I wasn't talking about a window air conditioner.

I was talking central air.

Are you an electrician?

You didn't SAY that though... what am I? Kreskin?

No, I'm not an electrician, that's why whenever a customer of mine asks for some wiring to be done, I call in one. BECAUSE as much as I know about house wiring, I know I don't know enough to attempt anything mmmouse wants to try.....
 
tboy said:
You didn't SAY that though... what am I? Kreskin?

No, I'm not an electrician, that's why whenever a customer of mine asks for some wiring to be done, I call in one. BECAUSE as much as I know about house wiring, I know I don't know enough to attempt anything mmmouse wants to try.....
If your not an electrician, maybe you should not be commenting on this thread.
 
I've got a bunch of euro machines and appliances in my house and they work on 240V. Motors are cycle dpendant, electronics are not because they always use transformers and rectifiers to convert to DC voltage inside.

You need to make sure your supply is correct, that it is indeed 220V or 240V (whatever your provider claims it to be). Bringing a line direct from your service panel, a red wire to one breaker and a black wire to another side by side will usually result in a doubled voltage. FI in doubt, if you haven't done this before, just DON'T. There are plenty of people around familiar enough with service panels to assist.

The basic result is that YES you can certainly use a euro electronic appliance without any hassle. I remember that even as far back as 1962 my father brought back a Phillips turntable from Holland and wired it up.
Doug
 
Meesh said:
Watt a charge I get out of threads like the current one where there's resistance to an idea.

DC what I mean?

(I know, my puns are revolting.)

Carry on....

No resistance.

Just people with a little knowledge.

You know what they say " A little Knowledge is a dangerous thing"
 
squirrelly04 said:
If your not an electrician, maybe you should not be commenting on this thread.
If we followed this logic, the lounge would be pretty empty.:D
 
tboy said:
As for 220/240 using smaller wire...that's funny! every circuit I've ever seen that provides 240V is 10 or 12 gauge

As already stated in this thread the gauge of wire required is based on the current that runs through it not the voltage. 14ga. is rated for 300 volts but you wouldn't know that because you're not an electrician right???

and the rest of the house is 14 or 16 ga.....

Oh really? The rest of the house is wired with 14 and 20 gauge. Please tell me where you have used or have had your electrician use 16 ga wire???? Oh wait...my bad you were referring to speaker wire right?? No...wait...*rubs temples* you meant putting new cords on appliances!!! Fuck...maybe I'm Kreskin?

Man I love how people come on here sprouting off shit like this.....

Me too!!
I particularly love when people post multiple times in a thread and attack posters when by their own admission don't know what the fuck they are talking about. Methinks they just like the sound of their own voice. :rolleyes:
 
Tangwhich said:
208v is only on 3 phase commercial applications. Homes are 120/240v single phase.


You are WRONG.


208 is a voltage which occurs on some 3 phase systems (120/208V)

Other 3 phase voltages are 277/460V (US), 480V, 347/600V

Yes, most businesses (commercial & industrial) use 3 phase power, however it is possible to have 3 phase power installed at some residences.

MANY condos (residential) are 120/208V


It may not make a difference if you have 208V or 240V.. a lot of equipment has a voltage tollerance of plus or minus 10%... but check the user's manual / specifications.

Also remember that the European equipment is designed to work on 50Hz (we use 60Hz)
 
Doug said:
I've got a bunch of euro machines and appliances in my house and they work on 240V. Motors are cycle dpendant, electronics are not because they always use transformers and rectifiers to convert to DC voltage inside.

You need to make sure your supply is correct, that it is indeed 220V or 240V (whatever your provider claims it to be). Bringing a line direct from your service panel, a red wire to one breaker and a black wire to another side by side will usually result in a doubled voltage. FI in doubt, if you haven't done this before, just DON'T. There are plenty of people around familiar enough with service panels to assist.

The basic result is that YES you can certainly use a euro electronic appliance without any hassle. I remember that even as far back as 1962 my father brought back a Phillips turntable from Holland and wired it up.
Doug

Thank you! That is the info I was looking for.
 
Don't forget to let us know what happens, mmouse. BTW, can I be your beneficiary?
 
One thing you have to remember with electronics... the power INPUT for the power supply is AC, but what it puts out to all the internal parts is DC. You might just be able to get around the problem by merely replacing the power supply.

That's what I would look into...

Is this a brand that is also sold in in any markets with 120V?
 
Doug said:
...The basic result is that YES you can certainly use a euro electronic appliance without any hassle.

It depends:

Yes, you can take a European 240VAC appliance and make it work here but not visa versa. Most 240V appliances from here will not work there.

The problem is as others have noted. The 240 VAC wiring here is -110 and +110 VAC. The euro wiring there is 0 and +240.

The problem is older euro gear that assumes the 0 VAC wire is ground then exposes it on metal parts. It works over there because 0 VAC is the same as ground.

If I take that same older euro appliance and connect it it here to 240 VAC, it will run, but the exposed metal parts will be at -110 VAC instead of 0. If I touch both a metal part on the euro appliance (-110VAC) and something that is really grounded like say a DVD player (0 VAC), I'm going to get electrocuted.

That being said
1) I haven't seen an appliance like that for a while, however it doesn't mean that they aren't out there. Those little old B&W TVs were notorious for this.
2) If there are no exposed metal parts it will likely be ok
3) Unless you are using this euro appliance where your dryer or stove is connected, its going to cost you a lot more to get an electrician to wire up a 240 VAC outlet than buying a transformer.
 
squirrelly04 said:
I don't think you know what you a talking about, maybe you should call an electrician!
Air conditioners are 240 volts. They don't have a neutral. How do they work? Maybe the electrons go into space?
I will preface my remarks by saying that I am not an electrician. I picture the current travelling along the hot wire towards the light or appliance and out along the neutral wire. 120 volt wire has a hot (black) wire, a neutral (white) wire and a ground. A 240 volt stove or dryer wire has 2 hots (one black and one red), one neutral and a ground. There is also 240 type wire that has two hot wires (red and black) that double as neutral wires depending on what phase the current is in at a particular point in time (changes 60 times a second). This latter type of wire is probably what you were referring to. I know it is used for baseboard heaters but I am not sure about central air. Can any electricians comment on my view. I know I might not be correct on the physics involved, i.e., the direction of the current, but is my conception about the two wire (plus ground) 240 volt cable correct?
 
tboy said:
As for 220/240 using smaller wire...that's funny! every circuit I've ever seen that provides 240V is 10 or 12 gauge and the rest of the house is 14 or 16 ga.....

Man I love how people come on here sprouting off shit like this.....

Wire size is based on amperage, not voltage. Items that usually use 240v in Ontario are high amperage units. That's why the wire is thicker. Comparing 2 items of the same wattage, the one using a higher voltage will use less current so doesn't require wire to be a large.

BTW, 16 gauge wire is not allowed in Ontario for electrical purposes.
 
Papi Chulo said:


You are WRONG.


208 is a voltage which occurs on some 3 phase systems (120/208V)

Other 3 phase voltages are 277/460V (US), 480V, 347/600V

Yes, most businesses (commercial & industrial) use 3 phase power, however it is possible to have 3 phase power installed at some residences.

MANY condos (residential) are 120/208V


It may not make a difference if you have 208V or 240V.. a lot of equipment has a voltage tollerance of plus or minus 10%... but check the user's manual / specifications.

Also remember that the European equipment is designed to work on 50Hz (we use 60Hz)

I was referring to houses. I've not seen a 208v condo myself, but admittedly I've only worked on a few of them.
 