You are partly correct, I should have said the UL label should have a C beside it. Sorry about that, I should have been more clear in what I said
 
C Dick said:
So what is knob and tube?
todays houshold wiring has the conductors all in one external casing, knob & tube was a system where the hot and neutral were seperate wires , and run through the studs & joists about 1foot apart from each other, where the wires passed through studs & joists there was a porcelain insulator(the tube) , the conections were made by twisting the wires together (the knob) , with no junction boxes,and no marrets,the connections were simply covered with cloth electricians tape. It wasn't really a bad system in its day IMO, but it was difficult to trace hot & neutral as both wires were normally black in colour, and there was no ground,
 
If you use equipment not approved by CSA in Canada it can/have to get special approval from the esa (electrical safety authority).
Just for the record residential(houses) wiring is single phase 120/240v http://www.eatonelectrical.com/unsecure/html/101basics/Module10/Output/BasicCircuitryandWiring.html
For most wire sizing in your home you should consult table 2 http://www.norantel.com/images/stories/pdf/copperconductorsraceway.pdf in the cec or oec if your using conduit it can get more complicated. WIRE SIZE IS BASED ON AMPACITY .
 
baci2004 said:
Thanks for the tip!

Question...would there be any added danger if I would to install the metal probe instead of the glass one, hold it in my right hand and use my left hand as a probe while the current flows through me?


Depends who you talk to. No added danger if everything is running properly and you use a GFI as an added safety. Watch heat build up in the unit since you are not holding it he heat will be less evident.

A more comfortable and slightly safer way to do it is:

1) Use a foot pedal to be able to turn it off easily (remember to wear shoes or flip flops. Most switches are grounded.
2) Connect metal probe to a wire to a nice roughly 2”x2” metal plate and put it in direct contact with your skin. Rubber bands holding it to your arm is fine (the one you use to touch ideally).
3) If you use it in this mode remember that sparks hurt. Try using a spoon, or other metal item.
4) Kissing is utterly incredible (on low settings) but watch out for metal dental work. I was reminded of that recently.
5) Be extra careful of metal beds, jewellery, etc that could concentrate the static charge.

Can also do it the other way. Plate on subject, and let electricity jump to you.

This should probably be in BDSM, but you asked the question here.

A Mod might move us there if they are feeling kind.
 
Papi Chulo said:
... approved for use in Canada...

Some folks here are US based. CSA= Canada, UL = US

Papi Chulo said:
Again.. that is not true as DC is more deadly than AC... 347V is also deadly....

BTW, 347 VAC phase-neutral is 600 VAC ph-ph. It's commonly used in commercial/industrial lighting.

Sadly, the two guys I know that did survived contact with 600 VAC each lost both of their legs. One guy was from the knees down, the other was total loss of use.

I know this isn't what you meant, but industrial DC systems have their own special hazards like hydrogen and acid. They use batteries about 4X the size of a car battery, each are about 1.2 VDC and are racked together to produce 125, 250 or 400 VDC. If you accidentally produce a spark while checking a battery, say by dropping a screwdriver that was in your shirt pocket when you bend over, you can ignite the hydrogen. The battery will blow up and shower everything with acid plus you still run the risk or electrocuting yourself.
 
Papi Chulo said:
Is it just me or does it seem like there is an awful lot of electricians on terb?


Not only electricians, but electricians that are trained in European 220 standards. Most North American electricians I know do not even know where to find the fuse on a European circuit.

<<< Not an electrician.
 
l69norm said:
I seem to remember that if knob and tube shows up in the paperwork for a home resale, the insurance company wants it removed and you would need to factor it into the negotiated price. It's about $1,200 per room. No insurance = no bank mortgage = no sale. It's the same for an oil furnace/ underground tank.

Maybe one of the TO real estate guys can confirm?

I'm not an agent, but it would depend on the neighbourhood I would think. In a lot of old areas - Beaches, Riverdale, High Park, Bloor West, Cabbagetown, the market is so hot that the sellers will simply tell you to pound salt on ANY condition. It's simply as is and whatever you don't like is your problem. If you don't buy it and fast, someone else will.

When I bought my place 11 years ago, the listing agent made it, "subject to inspection" and the vendor simply stroked it off. The only thing that stuck was no Urea Formaldahyde Foam Insulation.
 
data1960 said:
How true! I still do electrical work on the side (I help my buddy who is a licenced electrician). About 30% our work is swapping out old panels for modern panels. It's funny, he tries to convince the homeowners to take out the old knob and tube and virtually no-one would do it.

It ain't cheap, but if the home is a smaller bungalow, it's not killer expensive either, especially if we can start it in the same day we are there. For me, I'd be scared for my family, especially if a hack had tickered with the wiring.

Most home owners are cheap.

I have several friends living in older houses that are all knob and tube and when I tell them that they should get their houses rewired, they just roll their eyes, "there he goes again". I'm kind of known never to do any house reno work half assed and pretty much all of them are as half assed as it comes. Whatever is cheapest is all they are interested in.

As I previously posted, I had a good friend who's house CAUGHT ON FIRE due to old wiring and yet she still didn't want to pay to rewire the place properly.

Another friend said to me, "if I have a budget of 10,000 to spend fixing this place up, the last thing I am going to spend it on is wiring"

They'll spend 10 grand on a vacation, but won'd spend it on making their house safe, though strangely enough, they think it IS safe. All it usually takes is them hearing, "my friend is has had knob and tube in their house and it's fine" from someone they know. It's what they want to believe.
 
James: one of the main reasons ppl feel this way is because many homeowners these days are more concerned with how their house looks, not how it's built. Hence why you'll get 1010% ROI on new kitchens and bathrooms and not for things like double glazed windows, upgraded wiring, etc.

I belong to facebook and there was a thread on how new homes are shit and they don't build them like they used to. I took all kinds of heat for saying "thank GOD they don't build them like they used to....".....
 
Now I could be wrong here (and I know that people will be more than happy to point it out if I am :) ), but I was helping renovate an old building that had knob and tube wiring throughout. Before we changed all the wiring I noticed the little wheel in the meter was turning a lot faster than it was after, even though there were the same things plugged in (a clock, a coffee machine and a toaster).

Am I correct in assuming that the K&T style of wiring has more line loss than modern?

Oh yeah, before someone points it out, neither the toaster or the coffee machine were being used while I was observing the meter.
 
For anyone still interested, I wired my European device into my stove outlet and it works perfectly. For a permanent solution I will be running a 15A 240v circuit from the main panel.
 
mmouse said:
For anyone still interested, I wired my European device into my stove outlet and it works perfectly. For a permanent solution I will be running a 15A 240v circuit from the main panel.

Assuming you want to be legal.... run your 15/2 or 12/2 to a 220/240 plug. Then buy an male plug to fit into the hole.

Assuming you want the safest solution..... run the 14/2 or 12/2 to a european (British?)) female plug. They have a built in fuse or circuit breaker and will blow around 5 or 7 amps (I do not remember the exact rating)preventing fires in your house (not house wiring) if receiver shorts out.

By the way.... electricians in Canada are NOT trained on this type of stuff, so the various opinions are basiclay their 'common sense'.
 
Moraff said:
Now I could be wrong here (and I know that people will be more than happy to point it out if I am ), but I was helping renovate an old building that had knob and tube wiring throughout. Before we changed all the wiring I noticed the little wheel in the meter was turning a lot faster than it was after, even though there were the same things plugged in (a clock, a coffee machine and a toaster).

Am I correct in assuming that the K&T style of wiring has more line loss than modern?

Oh yeah, before someone points it out, neither the toaster or the coffee machine were being used while I was observing the meter.
If you plug your 2 prong plug in backwards, the meter runs backwards :p


The old knob and tube was rated at like 30 amps and you put a western union splice on it then soldered the splice. If you did not solder the splices you would get a greater resistance thus higher amp usage.
 
papasmerf said:
If you plug your 2 prong plug in backwards, the meter runs backwards :p

Lol, Is that the same sort of thing as reversing your fridge plug to heat stuff up? <grin>
 
Moraff said:
Lol, Is that the same sort of thing as reversing your fridge plug to heat stuff up? <grin>

Don't be silly that only works with microwaves
 
LordLoki said:
Assuming you want the safest solution..... run the 14/2 or 12/2 to a european (British?)) female plug. They have a built in fuse or circuit breaker and will blow around 5 or 7 amps (I do not remember the exact rating)preventing fires in your house (not house wiring) if receiver shorts out.

This is basically what I'm going to do. British sockets are rated up to 13A per outlet. The fuse is actually in the plug itself (the male part) and you are supposed to use the correct fuse for your eqipment - e.g. 1A for a lamp, 13A for a vacuum. Putting a double outlet on 15A breaker will be plenty safe.

I spoke to an electrician and when it comes to running 240v lines, red cable should be used instead of white.
 
mmouse said:
This is basically what I'm going to do. British sockets are rated up to 13A per outlet. The fuse is actually in the plug itself (the male part) and you are supposed to use the correct fuse for your eqipment - e.g. 1A for a lamp, 13A for a vacuum. Putting a double outlet on 15A breaker will be plenty safe.

I spoke to an electrician and when it comes to running 240v lines, red cable should be used instead of white.

Red cable? I thik I am heaing a le with a black covered wire and a red coveed wire instead of black and white? Yup. 14 gauge or 12 would be fine. Get least expensive one. Remember to get 15 amp double pole breaker for 220.
 
LordLoki said:
Red cable? I thik I am heaing a le with a black covered wire and a red coveed wire instead of black and white? Yup. 14 gauge or 12 would be fine. Get least expensive one. Remember to get 15 amp double pole breaker for 220.

He would need to use "Heatex" (red NMD90, containing a black & red).. or use 14/3 (use the black, red & ground - not the white).... it is the same price as 12/2

14/2 would be the least expensive as it contains less copper
 
james t kirk said:
...The only thing that stuck was no Urea Formaldahyde Foam Insulation.

It's been a while, but I think the vendor now has to declare "knob and tube" in the listing. If he doesn't, he may be liable to the cost of the conversion. The buyer's agent is suppose to advise the buyer of possible insurance issues and the home inspector is suppose to advise on the estimated cost. The buyer is suppose to adjust the offer by the estimated amount ($1,200 per room sticks in my mind)

Someone also told me that UFFI isn't a big deal anymore, but the clause is still there for liability reasons.
 