Surge protector for the house circuit panel

So in talking to a friend, he mentioned I should be concerned with how many KAs it can handle, his cousins said 80KAs should be sufficient, but my friend said 100KAs or more.

Anyone, anyone?
100KA's would be 100000 amps, your house panel won't be more than 125 amps, unless you have a really big house. He probably meant KVA's (kilo volt amps, or watts) and if your house has a 240 volt, 125 amp service, it would be 30 KVA.
As for where to buy a surge protector, Nedco, Westburne and Gerrie Electric are good places to go.
 
100KA's would be 100000 amps, your house panel won't be more than 125 amps, unless you have a really big house. He probably meant KVA's (kilo volt amps, or watts) and if your house has a 240 volt, 125 amp service, it would be 30 KVA.
As for where to buy a surge protector, Nedco, Westburne and Gerrie Electric are good places to go.

He is talking about how many amps the main surge breaker will open under in fault conditions. In sufficiently severe overloads, breakers will not trip. I've heard stories about these faults, but never actually saw one personally. (It helps to wire things safely and correctly.)

I would not skip on the interrupt rating. If you can get a higher rated panel, use it. This is not a place to use the minimum requirement, as Hydro's equipment is notorious for not consistently tripping in the event of a fault. Hydro needs to contend with frequent lightning strikes, and the extreme energies involved creates problems with fault protection equipment.
 
Fuses will not blow instantly until the load consumes 5 times the rated current, in this case 75 Amps. A fast blow fuse can take over 1/2 hour to blow against a 2 times rated current overload.

Circuit breakers are poorer overload devices than fuses.

It is likely that if you test brand new 15 (A) circuit breakers, most will not disconnect instantly against a 56 (A) load.

The instance i am talking about has been that way for over 3 years. The Forman is aware of it but does not want it fixed, they would have to change out the panel.
 
Dangerous.

No, he was right. Neutral and ground are bonded in the panel.

Even my new oven that I bought - the neutral and the ground were bonded right at the end of the wire tail where you need to hard wire it to a junction box.

Neutral and ground are both to carry the same potential - 0 volts.

The ground in a house will be connected to a copper water service, a ground rod right outside, or a buried ground plate. The neutral will run out to the street, but somewhere close to the transformer, it will be grounded through a ground rod as well.
 
He is talking about how many amps the main surge breaker will open under in fault conditions. In sufficiently severe overloads, breakers will not trip. I've heard stories about these faults, but never actually saw one personally. (It helps to wire things safely and correctly.)

I would not skip on the interrupt rating. If you can get a higher rated panel, use it. This is not a place to use the minimum requirement, as Hydro's equipment is notorious for not consistently tripping in the event of a fault. Hydro needs to contend with frequent lightning strikes, and the extreme energies involved creates problems with fault protection equipment.

I did understand what he was saying, I was just informing him it would be highly unlikely a house would require any equipment that would be rated for 80000 to 100000 amps.