The broken neutral is pretty nasty. Essentially, power comes into the house as 240 (V) with a center Neutral (Common) conductor, which corresponds to the 1/2 way point (240V * 1/2 = 120V). The 120(V) plugs around the house hook to the 240 (V) blacks, and the Neutral (Common) white conductor, which only contains one half of the 240(V) potential.
If you lose the Neutral, then any voltage between 0 and 240(V) can appear on any plug throughout the house. Often, the loads vary depending on which appliances are consuming current, and the precise voltage on any given load is unpredictable. Often 80-90(V) and 140-180(V) are seen on each side of the line.
The issues with many surge suppressors are:
(1) most surge suppressors are rated at 300(V) so they will do nothing, and
(2) most surge suppressors lack the wattage / power dissipation to blow a breaker, and will burn out rather than disconnecting the power.
Additionally, I suspect surge suppressor designers deliberately use 300(V) components so as to minimise warranty claims.
Another issue with broken neutrals is that they can be "flaky". People can endure a rather large number of equipment failures before anyone notices. Broken neutrals are very rare. However, when they occur, they are very expensive.
Isolation transformers can convert 240(V) into 120(V), and establish a new neutral. A self-regulating transformer can convert a wide range of input power levels into 120(V). Both transformers can be very effective at suppressing severe EMI disturbances, like nearby lightning strikes, by simply saturating and refusing to pass the energy into the secondary. A sufficiently close lightning hit will simply destroy everything in its path to ground, so the protection is not perfect.
In industrial settings, large motors are notorious for generating severe problems on the ground and neutral conductors. Measuring 300(V) and 70(A) on a ground conductor is not uncommon. Most PCs will not survive a neutral to ground voltage of 300(V). An isolation transformer will make neutral=ground again.
I'm not an electrical Engineer, but I'm trying to get my head around this broken neutral thing.
You've got a red wire and a black wire coming into a house. They come off the secondary side of the transformer at opposite ends of the coil, with the neutral (white) in the middle.
Devices that run on purely 240 volts (like my Central Air) only need the red and the black, they don't need the white. They then operate at 240 volts. Some things like ovens and driers have a neutral because some components of the oven (maybe the clock or control head) operate at 120 volts, but the burners probably operate at 240. Hence why you see a black, red, and white conductor in the cable.
Now I can understand if a neutral were to break you'd end up with 240 to your clock (say) on the oven and caboom.
But what I don't understand is say a conventional wall recepticle where you only have 2 conductors. A black and white. If the white breaks, you cannot have 240 volts because A) the circuit cannot be completed and B) you've only got one conductor coming off the secondary of the transformer, so you can't complete the circuit to get 240 volts.
I can only see how the broken neutral would affect major appliances where you've got both the black, the red, and the neutral coming in.
But I don't see how if you've got just either black or red and a neutral.
Disconnect the neutral on a single pole 15 amp breaker and your light just goes dark.
I'm Confused???
When I had the old 60 amp service at my house replaced with a 100 amp service, I recall the Toronto Hydro technician telling me that:
First you connect the neutral
Second one of the hot phases
Third, the other hot phase.
He didn't really explain it, but now I think I understand.
BTW, my house was built in 1920 and it had knob and tube wiring when I moved in. The old fuses were actually "fuse pairs" in a ceramic holder. They featured a fused hot AND a fused neutral. I'd never seen anything like that before.