Below is a scan of the Ontario Building Code, Section 9 (Residential) regarding Concrete Compressive Strengths.

You will note that 32 MPA is the minimum specified compressive strength for what the OP is proposing - not 20 MPA (Weekend Guy), not 25 MPA (Hammerstein).

35 MPA gets you a slightly better cement content.

End of story.

BTW, a good test for all you guys out there wanting to hire a Contractor to do some home Reno Work - "Do you own a current copy of the Ontario Building Code?"

No = HACK. I love how many Contractors run around spouting off about Code this and Code that, and they don't even OWN a Building Code.

Some independent contractors know these rules already from longtime experience, assuming the codes haven't changed. So not having a copy of the code doesn't necessarily mean they're quacks.
 

weekend_guy

New member
Aug 19, 2006
295
0
0
The mean streets of Bloor West
Below is a scan of the Ontario Building Code, Section 9 (Residential) regarding Concrete Compressive Strengths.

You will note that 32 MPA is the minimum specified compressive strength for what the OP is proposing - not 20 MPA (Weekend Guy), not 25 MPA (Hammerstein).

35 MPA gets you a slightly better cement content.

End of story.

BTW, a good test for all you guys out there wanting to hire a Contractor to do some home Reno Work - "Do you own a current copy of the Ontario Building Code?"

No = HACK. I love how many Contractors run around spouting off about Code this and Code that, and they don't even OWN a Building Code.


A couple of things:

1) You're telling the OP to use 35 MPa concrete and you're referencing the code for the compressive strength of unreinforced concrete, yet you're suggesting the use of 15M rebar at 300mm c/c. This is overkill.

2) The reference you make to exterior flatwork requiring a compressive strength of 32 MPa for unreinforced concrete is in the same category as garage floors and carports. This category would be subjected to loading from vehicles, permanent storage of heavy items, and anything else someone might cram into their garage or exterior storage area. The OP is asking about a concrete pad for a backyard deck. I'm not sure what he's planning on using his deck for, but I doubt there would be an F-150 parked there.

3) Section 9.16 speaks to Floors-On-Ground:

9.16.4.5. Compressive Strength
(1) Where dampproofing is not provided the concrete used for floors-on-ground shall have a
compressive strength of not less than 25 MPa after 28 days.
(2) Where dampproofing is provided as described in Article 9.13.2.7., the concrete used for
floors-on-ground shall have a compressive strength of not less than 15 MPa after 28 days.

4) Section 9.16.2.2. Support of Floors speaks to the fill requirements for floors-on-ground that will be subjected to freezing temperatures. The OP's concrete pad could likely fall into the category of Floors-On-Ground, and therefore the compressive strengths outlined in 9.16.4.5. should not be dismissed.

5) The OPSS spec for sidewalks requires 30 MPa unreinforced concrete, which is designed for live loads resulting from pedestrian traffic (not an insignificant loading!). Again, you are telling the OP to use 35 MPa concrete with 15M rebar for concrete pad under a backyard deck!

Bottom line: it's not the end of story as suggested by JTK, and further investigation and opinions are warranted to save you some hard-earned $$$.
 

james t kirk

Well-known member
Aug 17, 2001
24,032
3,879
113
A couple of things:

1) You're telling the OP to use 35 MPa concrete and you're referencing the code for the compressive strength of unreinforced concrete, yet you're suggesting the use of 15M rebar at 300mm c/c. This is overkill.

2) The reference you make to exterior flatwork requiring a compressive strength of 32 MPa for unreinforced concrete is in the same category as garage floors and carports. This category would be subjected to loading from vehicles, permanent storage of heavy items, and anything else someone might cram into their garage or exterior storage area. The OP is asking about a concrete pad for a backyard deck. I'm not sure what he's planning on using his deck for, but I doubt there would be an F-150 parked there.

3) Section 9.16 speaks to Floors-On-Ground:

9.16.4.5. Compressive Strength
(1) Where dampproofing is not provided the concrete used for floors-on-ground shall have a
compressive strength of not less than 25 MPa after 28 days.
(2) Where dampproofing is provided as described in Article 9.13.2.7., the concrete used for
floors-on-ground shall have a compressive strength of not less than 15 MPa after 28 days.

4) Section 9.16.2.2. Support of Floors speaks to the fill requirements for floors-on-ground that will be subjected to freezing temperatures. The OP's concrete pad could likely fall into the category of Floors-On-Ground, and therefore the compressive strengths outlined in 9.16.4.5. should not be dismissed.

5) The OPSS spec for sidewalks requires 30 MPa unreinforced concrete, which is designed for live loads resulting from pedestrian traffic (not an insignificant loading!). Again, you are telling the OP to use 35 MPa concrete with 15M rebar for concrete pad under a backyard deck!

Bottom line: it's not the end of story as suggested by JTK, and further investigation and opinions are warranted to save you some hard-earned $$$.
Uh, read what you posted.

An exposed slab is not damp proofed. And it’s not a concrete FLOOR. Therefore, you are incorrect again.

Yes, I told the OP to use 35 MPA concrete. The OBC calls for 32. Do you think that that is a huge difference? Really?

Uh, no.

35 MPA is readily available and typically spec’d by anyone in the industry who knows his ass from his elbow.

The OPSS allows for 30 MPA concrete for sidewalks you are correct (cause I posted that link as well). 30 MPA with 355 kgs of cement was the old MTO standard for everything. Now, they’ve gone to High Performance Cocnretes, etc – like 50 MPA and Silica Fume (neither of which I would ever recommend, even for a bridge) But they kept the 30 MPA for sidewalks.

BUT, the OBC calls for 32 MPA (not 20, and not 25) and since we’re talking a residential application, the OBC trumps MTO. However, it’s really splitting hairs because the MTO 30 MPA mix has 355 kgs of cement in it to resist freeze thaw damage, etc. and will come in around 40 MPA due to its high cement content.

Blah blah blah.

I’ve shown a scan of the OBC which clearly calls for 32 MPA concrete.

The 15 M rebar is based on my experience with mesh being for chumps and hacks and the cost difference would be minimal. Fibres help control shrinkage cracking (maybe), but they do NOTHING to prevent differential movement along a crack. Rebar (or arguably mesh) will definitely prevent differential movement and control cracking. You can add the synthetic fibres to the concrete for a few extra bucks and use it on top of the rebar.

I gave the guy a good long term design that will perform. If you think it’s wise to save maybe a grand on materials for s substandard design that will not perform nearly as well as mine – well, knock yourself out.

But don’t go for a permit – cause they’ll tell you you need 32 MPA.

No offense buddy, but I’ve never been one to do half assed anything. It only comes back to bite you in the ass.
 

james t kirk

Well-known member
Aug 17, 2001
24,032
3,879
113
Some independent contractors know these rules already from longtime experience, assuming the codes haven't changed. So not having a copy of the code doesn't necessarily mean they're quacks.
No, it pretty much makes them hacks in my eyes. It is IMPOSSIBLE to know the OBC by heart.

You can buy "Code and Construction Guide for Housing" from the gov't book store for $90.00. It's basically Part 9 (Residential) of the OBC in both an easy to understand version with helpful hints and a copy of Part 9.

For 90 bucks, there's no excuse not to own this if you're a Contractor.

Here's the link:
https://www.publications.serviceontario.ca/ecomlinks/510082.pdf
 

Cassini

Active member
Jan 17, 2004
1,162
0
36
4. Be careful insulating old masonry walls (rubble stone) or old concrete block walls. If you insulate on the inside, the wall will now be cold. The wall will wick moisture in the fall, then in the winter, since the wall is cold, the moisture freezes and blows apart the mortar or the block. The result is structural damage over time to your masonry foundation wall. Better to keep the wall warm in the winter through a bit of heat loss than to freeze an old masonry wall.
This is very important, and is rarely mentioned in many of the do-it-yourself books.
 

bebe

Well-known member
Aug 17, 2001
5,214
456
83
I don't know about that part of your statement. Perhaps for regular floors with modest reinforcement but I've seen thick pads or structural suspended slabs with a lot of rebar and they don't crack like typical saw-free floors.
Read the whole sentence:

If the slab is not sawcut within say 12 to 18 hours, the slab will curl and crack no matter how much or little rebar is placed within the conrete.
 

GPIDEAL

Prolific User
Jun 27, 2010
23,359
11
38
No, it pretty much makes them hacks in my eyes. It is IMPOSSIBLE to know the OBC by heart.

You can buy "Code and Construction Guide for Housing" from the gov't book store for $90.00. It's basically Part 9 (Residential) of the OBC in both an easy to understand version with helpful hints and a copy of Part 9.

For 90 bucks, there's no excuse not to own this if you're a Contractor.

Here's the link:
https://www.publications.serviceontario.ca/ecomlinks/510082.pdf
Contractor yes, but tradesperson or independent operator doing your patio hardly. Some moonlighters who work for larger companies will know about the proper specs for exterior concrete, but even the ready-mix companies will advise on the right mix because they usually ask what's it going to be used for.

The OBC isn't the be all and end all for concrete slabs (it's pretty scant when it deals with concrete flatwork - there's more info in the CSA standards). An experienced tradeperson doing just one aspect of a job like a slab doesn't have to be an engineer or memorize the entire OBC to necessarily know what's required for the work of his trade.

All said, I can't argue against your standard of care.
 

GPIDEAL

Prolific User
Jun 27, 2010
23,359
11
38
Read the whole sentence:

If the slab is not sawcut within say 12 to 18 hours, the slab will curl and crack no matter how much or little rebar is placed within the conrete.
I did read that part, and I'm saying that I don't necessarily agree when you say that if the slab is uncut, it will crack regardless of the extent of reinforcing.
 

Cassini

Active member
Jan 17, 2004
1,162
0
36
I did read that part, and I'm saying that I don't necessarily agree when you say that if the slab is uncut, it will crack regardless of the extent of reinforcing.
Concrete will not always crack. It can be laid in a manner that prevents cracking, and for appropriate applications cracking can be eliminated or confined to the surface layers.

It is difficult to do this, and as such, many concrete installations will crack. The saw cuts control the cracking.
 

wop

I'm Back
Feb 11, 2002
493
0
16
overlooking an old mill
like he said, but leave out the rebar and the sealer...saw cut depth to 1/3 the slab thickness

You want to use 35 MPA concrete with a 7% air entrainment with a slump of 75 mm.

Slab should be 150 mm thick and poured on top of a free draining material - like Granular A. If clay is present under the Granular, install weeping drains (holes down) below the granular layer to provide drainage.

Use 15 M rebar at 300 mm c/c located in the centre of the slab (hold it off the ground with concrete bricks) in both directions to control cracking.

Sawcut the slab down the centre, then in quarter panels in the other direction once the concrete has set up (usually within 12 hours) to control cracking (maybe).

Water cure the slab for 7 days (i.e. keep it CONTINUOUSLY soaking wet) to aid in hydration and to control shrinkage cracks (maybe)

Seal the sawcuts with a duoflex sealer once the curing is complete.
 

wop

I'm Back
Feb 11, 2002
493
0
16
overlooking an old mill
no fiber or rebar is needed for a slab on grade, (they don't use it in sidewalks) just a good base and saw cutting
 

james t kirk

Well-known member
Aug 17, 2001
24,032
3,879
113
no fiber or rebar is needed for a slab on grade, (they don't use it in sidewalks) just a good base and saw cutting
Some sidewalks are reinforced I can assure you. (Most are not.) But sidewalks crack and heave quite often. I doubt the OP would want this (I wouldn't) so rebar (or if you're cheap - mesh) will prevent heaving along cracks.

Sidewalks are also not saw cut, they tool joints into the fresh concrete - the idea being the same - to induce cracking at a known location - though it seldom works. Long pours will always shrink crack. It's a given.

The sealer is a joint sealer and is there to prevent water getting into the sawcuts and freezing and causeing damage.
 

oldjones

CanBarelyRe Member
Aug 18, 2001
24,490
11
38
Uh-oh!

I am in markham, where i want it to put it will be adjacent to the bungalow and behind the back of a double door garage will has a garage door leading to the backyard.
OK. Are you by any stretch, thinking you're getting advice about pouring a parking pad in your backyard, accessed thru your garage?

Your municipality (and your neighbours) might have an opinion worth checking out, as well as TERBians. And they might have offered different advice if you'd put the question that way.

But mebbe I'm just imagining?
 

slowpoke

New member
Oct 22, 2004
2,899
0
0
Toronto
You owe me dinner on the Danforth.....

1. WRT to your weepers, etc.

Use the white 4" perforated PVC pipe from Home Depot. (Do not use the thin walled black shit wrapped in filter sock - it's fucking junk.) You will see the white PVC perforated pipe in the plumbing section along side the black ABS pipe. This is the good stuff. You want to install the weepers so that the bottom of the weepers is at the same elevation as the underside of your footings (or foundation wall). Always install the holes down!!! (So many idiots install the holes up thinking that the pipe catches the water that way, it does not. The pipe simply forms a conduit for the water to flow through. Now the good part, you want to encase the weepers in 6" of either 3/4" clear stone all round, or crushed stone (but I'm not so sure about using crush with weepers to be honest). The entire thing has to be wrapped with a Geotextile cloth (or filter cloth) to prevent fines from contaminating the weeper over time. You then connect the weepers to a sump, or a storm water drain. (Do not connect to a sanitary drain!!).

2. WRT to waterproofing.

Waterproofing is what keeps the water out. Many are under the misguided belief that the wall (especially a concrete wall) will keep the water out. It will not. A house is not a boat.

Do not skimp on water proofing. You've gone to all the trouble of digging out, installing weepers, etc. it's fucking stupid to use cheap waterproofing. (And by cheap, I mean that black shit in a can that you see idiots putting on with a roller. Utter crap.)

I have seen this stuff both in use and at trade shows and I'm most impressed with it. I would recommend you hire them to do your foundation walls.

http://www.advancedcoatings.on.ca/rub-r-wall-airtight.html

3. WRT to Styrofoam insulation

It’s the best way to insulate your basement as you keep the wall warm and there is a thermal break on the outside of the wall. But........

Be careful insulating with Rigid SM foam on the outside of foundation walls, especially in your part of the town. Termites are well known to dig through foam creating tunnels to get into your house. If the foam laps any wood rim joist, the termites will dig through the SM, right to the rim joist and then they are in and you have a huge problem on your hands.

4. Be careful insulating old masonry walls (rubble stone) or old concrete block walls. If you insulate on the inside, the wall will now be cold. The wall will wick moisture in the fall, then in the winter, since the wall is cold, the moisture freezes and blows apart the mortar or the block. The result is structural damage over time to your masonry foundation wall. Better to keep the wall warm in the winter through a bit of heat loss than to freeze an old masonry wall.
Thanks James!!! Great information. Our foundation walls are triple brick, parged on the outside, and we have an old concrete walk running alongside the house in the driveway That walk has tilted & cracked over the years so now it traps water against the parging instead of channeling it away. Our basement hasn't leaked in the 15 years we've lived there but the only thing keeping the water out is probably that layer of parging. We started off planning to just rip & replace the driveway and the deck but now we're digging up half the house!! Hard to know where to stop.
 

69Shooter

New member
Jul 13, 2009
2,042
0
0
Any chance we'll see your project on a future episode of "Holmes on Homes"?
 

james t kirk

Well-known member
Aug 17, 2001
24,032
3,879
113


Here is a diagram on how to properly build a weeping tile system around your foundation.
 

bebe

Well-known member
Aug 17, 2001
5,214
456
83
I did read that part, and I'm saying that I don't necessarily agree when you say that if the slab is uncut, it will crack regardless of the extent of reinforcing.
It's true, if the slab area is large enough the concrete will crack. If you cast a slab 1m by 1m odds are it will not develop cracks. Now cast a slab 8 m by 12m without any sawcuts and I guarantee it will crack regardless if the slab is heavily reinforced or not. I have seen it happen about 100 times in the last 4 to 6 years alone, no lies. As I noted before, concrete contains water, one expects it to crack. The skill of the design engineer is to force the slab to crack within the deep sawcuts. By keeping the sawcuts relatively close and by weakening the slabs at the location of the sawcuts the chances are very high that the cracks will develop within the sawn joint. Another thing to keep in mind is that square slabs and square sawcut pattern that runs perpendicular to each other should be maintained as much as possible.
 

GPIDEAL

Prolific User
Jun 27, 2010
23,359
11
38
Concrete will not always crack. It can be laid in a manner that prevents cracking, and for appropriate applications cracking can be eliminated or confined to the surface layers.

It is difficult to do this, and as such, many concrete installations will crack. The saw cuts control the cracking.
Your answer to my reply is a bit off topic but I would never assume that concrete won't crack unless appropriate steps are taken. Yes, I know about control joints.
 